ENGR: Generators and leading power factor

The AList automation at control.com
Sun Oct 4 10:33:46 EDT 2009


==> Automation List post by jojo...
To view or reply to this thread: http://www.control.com/thread/1252671320#1254662858


------------------------------------------------------------------------------------
Re: ENGR: Generators and leading power factor
------------------------------------------------------------------------------------
If you are running with a real power load of 1600kW, you can go up to 1200kVAr on your genset. For other loads lower than 1600kW, try to find what is called the generator SOAR (safe operating area chart) for your generator (either in your manuals or from manufacturer). This chart will tell you how much reactive power can be loaded on your genset at a given value of real power.
------------------------------------------------------------------------------------