Re: ENGR: Eexd or Eexe juction box
------------------------------------------------------------------------------------
I just want to check with you whether inside the junction box only consists of terminal block connection and no external power supply unit inside it, and I assume the 24VDC is from external source and loop into the connections inside the junction box. If this is the condition, than you can use EExe junction box.
------------------------------------------------------------------------------------