Re: APPS: TMR Concept - A Query
------------------------------------------------------------------------------------
Hi Ritika,

Forget TMR, conventional design engineering prefers break to alarm/trip. Why so, when the problem is not in process but in system or associated hardware? Simply because, when the protection function is not in place, the preferred choice is shutting down the process. It may increase spurious trip rate but will drastically reduce dangerous failures which is catastrophic. Objective of design is to balance safety with availability.

Along with inbuilt diagnostics, voting in TMR provides additional level of validation through "threads of similarity", which allows the system to use in higher SIL rated applications.

If a TMR hardware is chosen for an application to eliminate nuisance trips only, simply you may follow 3-2-1-0 degradation as suggested by you. Otherwise by default it is 3-2-0 only, if it is not F&G application.

Hope above clarifies.

Regards.
------------------------------------------------------------------------------------


==> A Note from the Sender of this Message...
You are receiving this message because a subscription was entered for your address
for the Control.com Automation List.  To unsubscribe, send an email to us at 
forum at control.com requesting your removal from the subscription list.

This email was sent by: 
Control.com, Control Technology Corporation,
25 South Street, Hopkinton, MA, 01748, USA.

Copyright 2008 Control Technology Corporation. All rights reserved. 
Privacy and Legal Notices may be viewed at:
http://www.control.com/about.php


More information about the Automation mailing list